Hope this is the right place to get some answers… These ?'s are for a real full size steam locomotive, D&RGW 315…
1st some background, While undergoing our recent federal mandated 1472 inspection, It was noted that we have some issues with the lighting system. Apparently when restored in 2007 the wiring was a last minute issue, and was pieced together rather haphazardly. We have in the past 15 years had issues and problems, and now we can trace a number of these to the wiring issues. I opened a couple of junction boxes, and found wire nuts that were loose, and several that had come all the way off due to the vibrations of running, ( I have no idea who thought that you could use wire nuts on vibrating circuits)… I have taken on the project to re-wire the loco and bring it up to great current status.
Here is the spects.
Steam powered Turbine Generator. Just completed a $10,000 total re-wire and re-build. We really want to protect this generator.
Output 32VDC… 30 amps. My calc. says 960 watts max usage.
Draw:
Headlight 250 Watts & Taillight 125 Watts These are Tungsten bulbs ( both on at the same time, front or rear dimmed) = 375 Watts.
Number Board 1 ea. 5 Watt LED =5 Watts
Class Lanterns 2 ea. 5 Watt LED = 10 Watts
Steam / Air Gages 1 ea. 3 Watt LED = 3 Watts
Water Sight Glasses 2 ea. 3 Watt LED = 6 Watts
Cab Light 1 ea. 3 Watt LED = 3 Watts
Engineers Order Light 1 ea. 3 Watt LED = 3 Watts
My calc says that we will be under 410 Watts Max usage. Way under the load limit.
The 32VDC 250 Watt Tungsten bulbs, are no longer made worldwide, we have a small stock, but are seeking LED replacements, but until we can source them we will
be running those. The rest of the bulbs are LED from the Marine industry and are currently really available, they are rated at 10 - 80 Vdc, 3000K. All sockets are E26.
When the Loco was restored, a not prototype “Fuse Box” was installed. inside are just 4 circuits each with a 30A slow blow Glass Fuse in a E26 receptacle. 2 of these circuits have 16 gage wire ( scary huh?)…
Here is what I’m proposing to do… PLEASE JUMP IN AND TELL ME I’M About to do something wrong, if you think I’m making an error…
I Will build a fuse box ( wood looking old ) and install a 30 Amp resettable breaker coming directly off the Generator to protect it from overload. I will install in the front of the box a AMP Gauge, and a Voltage Gauge, so we can tell exactly what is being used.
For:
Headlight& Taillight, install 15 Amp resettable circuit breaker and use Copper Stranded 12 AGW wire.
All Other Circuits Individual 5 Amp resettable breakers and use Copper Stranded 14 AGW wire.
https://www.amazon.com/gp/product/B0CPKQTBGL/ref=ox_sc_act_title_8?smid=A24LFDN3EFRMHH&th=1
All connections will be crimped and/or soldered with waterproof Heat shrinked connectors.
PLEASE Give me any and all advise, I’m NOT and electrician, but I think I understand enough to make mistakes…
Thanks
Dave T.